I have installed 4 5kw inverters as recommended, 8 in apart. First two 2P0 second two 2P2.
The multi pin cable that has to connect unit 1 to unit 4 is too short by a few feet.
What to do??
I have installed 4 5kw inverters as recommended, 8 in apart. First two 2P0 second two 2P2.
The multi pin cable that has to connect unit 1 to unit 4 is too short by a few feet.
What to do??
thanks to Dante fro Eco-worthy I now have the extra parallel connector to tie all 4 inverters together. Not fully wired yet but sooon.
As someone with training in electrical engineering, I would say that extending a multi-contact cable is not recommended, as it may disrupt the synchronization of the inverters. The best solution is to rearrange the inverters so that devices 1 and 4 are closer together. An alternative is to order an original longer parallel cable from the manufacturer. The main thing is not to take matters into your own hands and try to solve the problem with improvised materials, as this will, at best, damage your equipment.