I recently installed an Eco-worthy 3500w, with one eco-worthy 100ah server battery, and 2x 440w PV for a total of 880w-DC.
Currently set up open-loop with desired values for "boost", float, and recover voltages.
"mains" are connected to Generator, to be fired up manually if and when needed.
PV, inverter, and battery all seem to be working ok..... Big problem is I cannot get the Generator to add more than 500watts to the battery no matter what I do with various settings. I want 10a=1200watts, and cannot get anything other than 500w
Any ideas? could this be be because I do not have BMS communication set up between inverter and battery ? or a bug ?
| [01] | UTI | "mains" (Gen) priority, inverter when no AC in present | |||
| [04] | 47.2 | battery to AC-in setpoint if [01]=SBU/SOL, n/a if UTI | |||
| [05] | 56 | AC-in to battery setpoint if [01]=SBU/SOL, n/a if UTI | |||
| [06] | SNU | PV & AC-in hybrid charging | |||
| [07] | 80a | max PV + AC-in current | |||
| [08] | LF16 | batt type | |||
| [09] | 57.2 | "boost" voltage (end of charge) | |||
| [10] | 10m | Veoc hold time | |||
| [11] | 54.4 | Vfloat (top), discharges to [35], and recovers | |||
| [14] | 46.8 | LV batt alarm | |||
| [15] | 46 | LV batt output OFF | |||
| [28] | 10a | Max AC charger current | 1200watts desired, getting 500 max | ||
| [32] | SLA | open loop, no comm inv to battery | |||
| [33] | PYL | battery protocol if [32]=BMS, otherwise NA | |||
| [35] | 50 | LV batt recovery output ON | |||
| [36] | 80a | max PV current | |||
| [37] | 53.2 | recover to Vfloat [11] after full charge [09], Vfloat (bottom) | |||