5000W off grid issue


  • I purchased a 5kw Solar off-grid inverter and two Power Mega 314 AH Lithium Batteries.

    I had no issue with setting them up. I watched a video from you support team to change setting 32 to 485 for comms and setting 33 to PYL.

    I am about to run small appliance with no issues.  I can run a 20 gallons hot water heater that pulls 15 ac amps. I can also run a 7500 BTU that pulls 6 ac amps.

    When I try to run a 15000 BTU ac I get a fault 05 – Battery over voltage protection. It kicks on for a few secs then start making power again. The ac unit on start up will serge to 22 amp then kicks down to 10 running amp. I used a watt meter to test.

    From what I can tell, the 5kw Solar off-grid inverter has the specs to run it.

    What do you all suggest adjusting or recommend?



  • @eric dickman

     

     dude That startup surge could be the problem, even if the AC runs at a much lower amperage once it's running. Compressors can draw a lot more power for a few seconds when they first kick in, and that sudden demand can cause issues with the inverter or battery communication.

    I'd check the inverter's battery voltage readings, BMS settings and surge capacity before changing any settings. Since you're getting fault 05, I'd also contact Eco-Worthy support to confirm what that fault means for your specific inverter and battery combination.

    Does the fault happen every time the 15,000 BTU AC starts, or only when other appliances are running at the same time now?

     