5000w 48v hybrid inverter configuration question


  • Can I configure it to (1) make sure no power is ever fed back to the grid, and (2) limit amperage it will draw from grid input to 30 amps ?



  • Not sure about the feed back to Grid answer.
    I don't see anything about limitied grid input power. You can set #28, Charging under Grid Electricity Value which should limit it bypass current plus the charge current (you can set)

     


  • Yes, most 48 V 5 kW hybrid inverters can be configured for both.

    1. Preventing export to the grid:
      Look for a setting like “Zero-export,” “No-feed-in,” or “Grid-feedback = Off.” When enabled, the inverter will only supply your loads and will not push any power back to the utility.

    2. Limiting grid input current:
      There is usually a parameter such as “AC input current limit,” “Grid charge current,” or “Max AC draw.” Set this to 30 A (or whatever your Google Doodle Baseball circuit allows). This caps how much current the inverter pulls from the grid for charging + load support.

    Exact menu names vary by brand, but nearly all hybrids support both functions.


  • Hi, new to solar and need help with the settings this hybrid inverter.  Can someone please tell me what all the settings need to be with running only solar, no grid?


Please login to reply this topic!